mixing valve

Options
Dan_18
Dan_18 Member Posts: 20
Can I use a 1/2 inch taco mixing valve to fead four loops of 3/8 onix tubing 25 feet per loop? Thanks for your response in advance.

Comments

  • Dan_18
    Dan_18 Member Posts: 20
    Options
    mixing valve

    Im sorry I ment to type four loops of 3/8 onix 50 feet each not 25. Im suprised no one has answered my question yet. I just need to know if that size valve would be ok, the 3/4 valve`s cv rating is not much more it seems like the one inch valve may be oversized. Im using a Grundfos ups15-58fc circ 3/4 supply and return up to the mixing valve.A4T254
  • Paul Pollets
    Paul Pollets Member Posts: 3,656
    Options
    Loop length

    Each loop could be 150 ft, no problem. You could do this with a 1/2" zone valve. The 15-58 is OK at low speed, the Alpha pump would be better, as it can pump at much lower speeds.