aquapex for heating

BOONE
BOONE Member Posts: 1
Found out that my radiant heating system has aquapex that is non barrier. Does anybody know have a solution? Can you install a 95% boiler with stainless/ no metal and be fine? Or is there another fix? Thanks.

Comments

  • EricAune
    EricAune Member Posts: 432
    edited November 2009
    Aqua PEX

    The best way is to isolate the tubing from the boiler system by using a flat plate heat exchanger.  An additional circulator (stainless or bronze), expansion tank and air eliminator is needed for this.  Consider installing a strainer on the inlet of the plate hx.



    Whether you decide to add a plate hx or not a system cleaner should be used to remove any residue in the PEX tubing.  Check this out: [url=http://www.rhomarwater.com/media/2008/10/rhomar_hydro_9100_flier_ii.pdf]http://www.rhomarwater.com/media/2008/10/rhomar_hydro_9100_flier_ii.pdf
    "If you don't like change, your going to like irrelevance even less"
  • NRT_Rob
    NRT_Rob Member Posts: 1,013
    depends on the boiler

    Triangle Tube says you can use open oxygen systems with their boilers. the 110 solo an excellence have cast iron pumps built in that need to be replaced, but otherwise, no problem. make sure you don't use cast iron outside the boiler.
    Rob Brown
    Designer for Rockport Mechanical
    in beautiful Rockport Maine.
  • Paul Pollets
    Paul Pollets Member Posts: 3,656
    Huhh?

    Where does it say Triangle Tube boilers can be directly connected to an open system?  Here's what I found from their online documents:

    NOTICE

    Do not install the Excellence water heater on

    any application if the boiler piping contains

    non-oxygen barrier tubing or if the boiler

    piping is considered an “open system”.

    Exposing the outer tank of the Excellence

    water heater to oxygen contamination will

    lead to premature tank failure and denial of

    the warranty.

     



  • EricAune
    EricAune Member Posts: 432
    Consider protecting your investment

    The high cost of any appliance should cause pause when knowing the damaging effects this tubing can pose to all system components.  Just because the hx is stainless does not protect other components (flow/temp sensors etc.) of these high buck boilers. 



    Isolation from the system is the safest way to prolong the life of a new boiler in this situation, not the least expensive now but could definitely save you a lot of money & headaches later. my two cents...again.
    "If you don't like change, your going to like irrelevance even less"