HB Smith efficiency question
new homeowner
Member Posts: 1
I moved into a new place over the fall and had the gas boiler serviced recently. The HB Smith boiler (GHB2W6)only tested at an efficiency of 74.8%. I thought that was low, especially since my old place had an ancient American Standard boiler converted to gas that had an efficiency rating of 79.5%. Any thoughts on this? It is a hot water system and the Fyrite analyzer readout showed:
efficiency 74.8
excess air 77.1
stack temp 451
primary temp 34.2
o2 9.7%
co2 6.3%
co 24 ppm
co air free 45 ppm
The technician who worked on the system was surprised at the low rating as well.
efficiency 74.8
excess air 77.1
stack temp 451
primary temp 34.2
o2 9.7%
co2 6.3%
co 24 ppm
co air free 45 ppm
Looks like it isn't tuned properly. Too much excess air.
Ron0 -
agreed
stack temp is high, so check excess air and have him check the manifold pressure, you may have too much input but your O2 and CO2 are off that looks more like excess air than an air leak.0 -
lot's of Old boilers test high eff ..
due to improper measurement techniques
don't be fooled0 -
Analyzer efficiency
Odds are if you are going by analyzer calculations, your new boiler is more efficient than the old. Analyzers can fake the efficiency and in reality the higher the calculated efficiency the more possible the actual operating efficiency is lower. The O2 readings is slightly high indicating too much draft or under-firing.0
- 86.8K THE MAIN WALL
- 56 Biomass
- 108 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 69 Pipe Deterioration
- 959 Plumbing
- 385 Solar
- 15.3K Strictly Steam
- 43 Industry Classes