Burner insertion on Buderus DV w/ Riello?

Saggs
Member Posts: 174
Just finished installing a Buderus GB115-34 w/ a Riello BF 5 burner set up for Direct venting. The burner came out of the box with the mounting flange set for the burner end cone to be 4 1/2 to 5" into the combustion chamber. I always thought they were slightly less than flush and thought this was kinda odd? I have put in other smaller Buderus DV's and thought they were flush. The wholesaler talked w/ the Buderus rep and he said this 5" or so dimension was correct. Does this sound right? and is it only particular with the 5 section?
0
Comments
-
Insert depth
The insert depth of the Riello F5 and BF5 series boiler on the Buderus G115/5 section boiler is ten inches. Measure from the end of the blast tube ten inches, then lock the flange. The tube should be into the heatexchanger about five and a half inches. It has been like this for many years.0 -
Sounds good, thanks again Joe! I appreciate the quick response. You gave me a tip last yr about upping pump pressure and changing nozzle size on a GB215/4 which worked great-No call backs at all-Thanks0
This discussion has been closed.
Categories
- 117.6K All Categories
- 82.8K THE MAIN WALL
- 2.7K A-C, Heat Pumps & Refrigeration
- 43 Biomass
- 403 Carbon Monoxide Awareness
- 8 Chimneys & Flues
- 1.6K Domestic Hot Water
- 4.3K Gas Heating
- 107 Geothermal
- 148 Indoor-Air Quality
- 2.7K Oil Heating
- 45 Pipe Deterioration
- 681 Plumbing
- 4.8K Radiant Heating
- 353 Solar
- 13.3K Strictly Steam
- 2.9K Thermostats and Controls
- 48 Water Quality
- 31 Industry Classes
- 65 Job Opportunities
- 11 Recall Announcements