Buderus GB124
Joe@buderus_2
Member Posts: 302
The GB142 is only approved to be vented with 3" schedule 40,PVC pipe (Foam core cannot be used for the vent) . The use of stainless steel vent material is not approved. The PVC pipe can be run up to the top of the chimney and the fresh air can be taken from the room or the side wall.
Buderus GB124
Is there a problem exhausting this boiler up a 30 ft chimney thru a 3 inch Stainless steel liner?0 -
If we take room air will that allow us to extend our vent lenth?0 -
Installation Manual
What did it say in the manual?0 -
Chimney venting
I ran both the air supply and flue up a cheminey worked out awesome here are some pics0 -
Vent Length
The venting length on the GB142/24, 30 & 45 is 100 "running" feet, the model 60 is 60 feet. There is not approvals to extend the venting further if room air is used.0
- 85.2K THE MAIN WALL
- 55 Biomass
- 73 Chimneys & Flues
- 129 Geothermal
- 3.3K Oil Heating
- 61 Pipe Deterioration
- 884 Plumbing
- 5.9K Radiant Heating
- 376 Solar
- 14.7K Strictly Steam
- 59 Water Quality
- 49 Industry Classes
- 89 Job Opportunities
- 28 Recall Announcements
