Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
One for the oil burner guys
Mikey B
Member Posts: 9
You should never paint the inside of any air tube. You are just reflecting more light for the cad cell to read and can cause major problems down the road. On your next call with these guys show them this service pratice. When boiler running do an ohms reading on cad cell. Close the air slowly to burner and watch the ohms creep down. this will prove the theory that you should not paint air tube, It's a band aid for a major problem. Just good quality trouble shooting will fix the problems.
0
Comments
-
Okay guys, time to get some opinions on one of my pet peeves. Why would anybody paint the inside of the blast tube silver on an oil burner??? I have seen this several times (guys in the company I work for do it). They will change the spray pattern, firing rate, or angle, then to improve the flame signal spray the blast tube silver. These are not what I would consider to be older burners, most of them have been installed within the past 10 years. Personally I think it's a liablity, but the boss has no issues with this practice. What do you guys think?0 -
I think
they need to check their OEM Spec Guides if the burners were matched to the boilers. In some cases down-firing is OK but you need to do it carefully.
In the Beckett class today, this subject came up and the instructor condemned the silver paint practice.
If something goes wrong, who would be responsible?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
exactly my point!!!! Thank you!!!
Typically they do this on OEM equipment, claiming the burner runs better with the changes, but I don't see it.0 -
Are they using digital combustion analyzers properly?
That's the only way to know for sure how a burner is running.
I wouldn't be surprised if they aren't............
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
I wish we had those. We're still using the old school Bacharach kits with the Fyrite. Electronic is much nicer though, I have used them with a previous employer. Can't convince the boss that they're better.0 -
Silver paint
Silver paint, white paint......... It shows a brighter light to the cad cell. So, instead of locking out when there is a poor flame , it will continue to run until the boiler soots up and smokes up the basement.
It is a band aid fix. If the cad cell ohm reading is off the cause should be determined. Not a paint job. Some wannabe burner men paint all of them out of habit. Why? because the "old guy" did it that way.0 -
But what I will never understand is why change anything when the burner was running fine when it was set up to OEM specs??? why fix what ain't broke???0 -
another peeve
I have known guys always have to wrap thermostat wire around a screwdriver, or plier handle and make a lot of spiral curly cues before going into the wiring device... because it looks neat.
Then I tell them how they are creating an induction field and I start getting the caveman stare
Cosmo0 -
and another
This is a big one.
Guys who replace a boiler, and leave the 30-40 year old oil supply line there, and just change the General 1A25A filter cartridge.
hey cheapskate, charge a couple bucks for a new oil line from the tank, and give your customer a good filter, like a Garber. Or at least a low micron filter insert for the General.....
Or here is another one, I was taught to always have a new spare nozzle for the burner left on the job. Every time you do a tune up, replace it. Then in an emergency, or if you don't have one in the truck you have the right nozzle to give the customer heat on a single digit night. It is one of the unwritten rules of the trade in my opinion.
Cosmo0 -
It always amazes me how creative contractors can get to minimize nuisances to themselves. The fact that they are using antiquated combustion test equipment shows they have no real commitment to accuracy. They are doing no favors to the customer other than costing them more fuel and potentially making the equipment more dangerous. The things they are doing, other than painting the air tube, are not necesarily bad things. They just don't have any accurate way of verifying what they are doing.0 -
The old silver paint trick. What is now condemed was considered a good "trick" years ago to make a burner run.
A lot of things were done in the old days that would be condemed today--thats progress.
Personally, I never was comfortable with the paint idea and I don't remember ever doing it but it was fairly common practice years ago. I agree with Bill, it could allow the burner to run with poor combustion.
Ed0 -
Paint
I think that the silver paint trick started in the 70s when a lot of older equipment was being retrofitted with retention head burners. Sometimes, we had to use a long blast tube to get around some obstruction on the front of the boiler. There was also the issue of the heat from the front of those old monsters reaking havoc with the transformers, so we wanted them at a (cool) distance. With that, the light was often far from the eye, causing nuisance lockouts.
Nowadays, the painting is unnecessary. I would rather see the squirrel cage blower get brushed out, and air tube cleaned well, as that is often overlooked.0 -
Induction Field
Since the current is comming and going to most controls,wouldn't it cross the other out?0 -
Good Point
The practice started with the long blast tubes use in retrofitting obselete boiler like the down fired GE. They also used a speical narrow tube on a Beckett.. That set up, still out there today ....you give the sign of the cross if it is still running ... Any long tube gives trouble to a stock cad cell even on a Riello.. Some guys used paint or moved the eye further down on the draw assembly closer to the fire..0
This discussion has been closed.
Categories
- All Categories
- 85.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 424 Carbon Monoxide Awareness
- 72 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 129 Geothermal
- 160 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 878 Plumbing
- 5.9K Radiant Heating
- 375 Solar
- 14.6K Strictly Steam
- 3.2K Thermostats and Controls
- 58 Water Quality
- 49 Industry Classes
- 89 Job Opportunities
- 28 Recall Announcements