Taco RMB-1 sesor
bovide_4
Member Posts: 161
which I have strapped to the radiant supply manifold always reads 10 degrees hotter on the screen than the probe thermometer I have next to it. There is insulation around the sensor. What should I look for?
EDIT: d-oh! "sesor" (why did I write like I have a lisp?)
EDIT: d-oh! "sesor" (why did I write like I have a lisp?)
0
Comments
-
Check the resistance........
...........of the sensor itself. It's a typical Tekmar 10K resistor.
hb
"Radiant Whisperer"
http://www.heatinghelp.com/getListed.cfm?id=304&Step=30