How to control supplemental heat with radiant floor
Steve Garson_2
Member Posts: 712
I have a master bedroom heated with radiant floor heat. The north wall is very high, since there is a cathedral ceiling. Supplemental heat in the form of a baseboard radiator on the wall was installed for those very cold days, which are rare, controlled by a second thermostat.
What I don't understand is how to properly control the baseboard. If the baseboard is heating, the radiant thermostat shuts off which makes the floor go cold. Can someone suggest the proper way to control this arrangement?
Thanks
What I don't understand is how to properly control the baseboard. If the baseboard is heating, the radiant thermostat shuts off which makes the floor go cold. Can someone suggest the proper way to control this arrangement?
Thanks
Steve from Denver, CO
0
Comments
-
Use a two stage tstat
and when the temp dropps two degrees cooler it then pulls in the supplimental heat0 -
Steve
I am sure there are better ways but here is the simple "cold days manual intervention option". I would just turn down the water temps for the floor a touch and set the floor t-stat to 75 and the Baseboard t-stat to 70 or what ever your choice may be (as long as there is a suitable difference between the two). That way the floor heat always stays on and the baseboard takes over if the floor can't keep up. The zone difference between the two t-stat settings keeps the floor from turning off.
Tom0 -
2 stage
stat..tekmar 512 w/ slab sensor to maintain floor temp0 -
2 Stage T-Stat
The best solution is one that is already given. A 2 Stage thermostat. The zone should already be set up on its own pump. Connect to W2 on the thermostat and whenever the floor cannot keep up it will call on W2. When satisfied W2 will drop out.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements