Steam boiler piping
Christian Egli_2
Member Posts: 812
Well, it's not like you can go anywhere else with the spill trap discharge, is it? Pouring it down the drain would be a shame.
Is this a single boiler setup?
If you have more than one machine all connected to the same header, the spill trap is necessary, and has to pour into the return system.
If it's only one boiler you have, then I don't see the point of the spill trap at all. If you're having overfilling, it's only because the condensate pump deliver unwanted water. [I'm also assuming you've beaten all the dirty water avenues]
To reign in the ill-mannered condensate pump, try first playing with the on-off level switch, making it run more often but shorter. Or convert the pump to a feeder pump, command it from a boiler level control. In this last case, you'll also need to observe the tank capacity itself, it might need to be increased and it might need a place to spill. All this should be real easy.
Also, is the condensate pump really necessary. Could some piping modifications make it totally unnecessary?
Is this a single boiler setup?
If you have more than one machine all connected to the same header, the spill trap is necessary, and has to pour into the return system.
If it's only one boiler you have, then I don't see the point of the spill trap at all. If you're having overfilling, it's only because the condensate pump deliver unwanted water. [I'm also assuming you've beaten all the dirty water avenues]
To reign in the ill-mannered condensate pump, try first playing with the on-off level switch, making it run more often but shorter. Or convert the pump to a feeder pump, command it from a boiler level control. In this last case, you'll also need to observe the tank capacity itself, it might need to be increased and it might need a place to spill. All this should be real easy.
Also, is the condensate pump really necessary. Could some piping modifications make it totally unnecessary?
0
Comments
-
Steam boiler piping
Smith 28A Steam Heat
Is "overflow trap piping" (to the condensate tank) always a good idea? I am considering this per Smith I/O manual. Presently the systems experiences high water levels in the boiler. The water makeup is working correctly.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements