let's talk numbers
Timco
Member Posts: 3,040
water heater reading: Eff:82.3, Excess air:55.2, stack temp:320, pri temp:74, delta:---, O2:8.0, CO2:7.3, CO:4, CO air free:6, draft:-0.01wc..........and now the boiler Eff:81.8, Ex air:72.7, stack temp:318, pri temp:82.1, delta:----, O2:9.4, CO2:6.5, CO:9, CO airfree:16, draft:0.00wc. Boiler is WM CGA gold, and water heater is a GE....both nat gas. Took these numbers after stack temp leveled off.
Am I getting these readings correct? First tests with the new 125 pro. I have a lot of reading to do...and classes scheduled.
T
Am I getting these readings correct? First tests with the new 125 pro. I have a lot of reading to do...and classes scheduled.
T
Just a guy running some pipes.
0
Comments
-
Anyone? Are these numbers in the ballpark? One has to start somewhere, and I am doing this by the book...
TJust a guy running some pipes.0 -
IMO
Water heater looks OK. Boiler apears a little off. O2 should be 7 to 9%. also, you should always have a negative .01 to -.02 draft at least. That .00 draft is no good.
If you want some readily availble reading material on combustion testing, check out the Bacharach Traingin Room at:
http://bacharach-training.com/0 -
Sooo..
If I have low draft, that would mean I could use some extra combustion air, as there are only 2 45* bends in a very short distance for the vent...but the high O2 says I have excess combustion air/draft??? Can the shutters be adjusted to lower the primary air and get some combustion air in there? The furnace room is open to the entire basement of a 1910 house...pleanty of leaks.
Thanks,
TJust a guy running some pipes.0 -
Combustion is occurring
and your CO numbers are not high. That would put "combustion air" out of the running.
What is the base pressure of the CAZ?
Mark H
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
CAZ? That's a new term for me...Still learnin'.
TJust a guy running some pipes.0 -
You might look to your chimney for the draft.
Any leakage in the chimney? Clean out doors. Are the vent connectors properly sized?0 -
175,000 BTU unit with 6" all the way...just less than 5 feet or so, with one 90 and one 45. Chimney was re-tuck pointed a few years ago but has no liner.
TJust a guy running some pipes.0 -
An unlined chimney
doesn't meet the National Fuel Gas Code.
There is an exemption if you replace existing equipment with equipment that is "similar type, input rating and efficiency." In other words you need to have the chimney lined.
The inner area of the chimney can't exceed 7 times the area of the smallest draft hood or flue collar connected to it. If you have a 3" draft hood on a WH the max flue size is 7x7 or 49 sq in.
Although I can't put my finger on it at the moment I don't believe you can use an unlined exterior chimney if you follow the NFGC (NFPA 54).
If you have poor draft the chimney is the likely culprit.0 -
It is
Combustion appliance zone.
Darin0 -
Will the fyrite pro 125 measure this? I ordered the optional differential pressure kit, but it will be a week.
TJust a guy running some pipes.0 -
Would the liner be the same single wall galvi as the boiler vent? Would the boiler 6" tie into a T in the chimney? What would the ideal cap be? Here in SLC I don't think a single chimney is lined except for when a fireplace insert is installed (enclosed pellet burner type)AND a permit was pulled.....
TJust a guy running some pipes.0 -
It depends
Is the chimney interior or exterior? If exterior, B-vent in an unused chimney flue meets NFPA 54.
We generally turn lining over the another company and they typically install aluminum or SS flexible liners. A single wall galv pipe may be acceptable if the chimney is interior but I haven't looked that up.
NYS WC is hell on contractors that have employees use ladders or get on roofs.
You may want to go to www.nfpa.org. You can download the latest books in pdf format. I think they're around $30 or so. Nothing beats having the knowledge and being able to back up your statements when the HO says, "How come none of the other contractors mentioned that?" "I don't know, ma'am. I guess they don't know or don't care."0 -
Give me a call
Certainly keep posting here - alot of valuable info for everybody.
Also, feel free to give me a call (it's part of what I do for Bacharach)
412-576-13500
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements