furnace fault
bernie_5
Member Posts: 2
FURNACE FAULTS OUT AFTER REACHING SET TEMP ON THERMOSTAT.MAIN BLOWER&INDUCER BLOWER STAY RUNNING. MANUAL SAYS THIS INDICATES THAT FLAME WAS SENSED WHEN THERE WAS NOT A CALL FOR HEAT.WITH THIS FAULT CODE THE CONTROL WILL TURN ON BOTH THE INDUCER MOTOR AND SUPPLY AIR BLOWER.THIS FAULT WOULD TYPICALLY BE CAUSED BY A GAS VALVE THAT LEAKS BY OR IS SLOW TO CLOSE.I PUT NEW GAS VALVE ON STILL HAVE SAME PROBLEM.HELP,THANKS IN ADVANCE
0
Comments
-
hmm...
gas valve is getting voltage when it shouldn't...board ? / Save that old valve.0 -
check stat and paperwork
If you have not aready done so check the stat. I would take the 4 or 5 stat wires off the furnace terminal strip and just jumper R to W to start the call for heat and then just take the jumper off to see if the problem repeats. Also, it is normal for allot of furnaces to have the blower and inducer run for awhile after a call for heat ends, the blower to cool off the heat exchanger and the inducer to post purge to dry out the heat exchanger and intake air box.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements