    I have a customer with a large 2 pipe steam system. 3 of regulating valves at the radiator are blowing a lot of steam. I assume the packings are shot since trying to tighten them did nothing. Can these typically be repacked? If so, what do you recommend using?
  • Al Letellier_9
    Al Letellier_9 Member Posts: 929
    steam valves leaking

    Yes, typically you can repack them. Best to use a graphite packing material. Teflon string packing can also due the job but doesn't seem to stand up as long. You can get graphite at any good supply house or a packing and gasket dealer.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Steamhead (in transit)
    Steamhead (in transit) Member Posts: 6,688
    Paul, you may find

    that these are "packless" valves. If so they will have to be rebuilt. Tunstall supplies rebuild kits for most valves.

    www.tunstall-inc.com

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Paul Fredricks_3
    Paul Fredricks_3 Member Posts: 1,557


    I checked out the valves today. I take off the cap nut and can then pull out the stem. It sits on a spring and the stem has a flat surface that mates to the bottom side of the cap nut. Seems almost like it should be a lapped seal. I can push the stem down a bit and put in a line of teflon rope. This seemed to make the valve feel a bit better, but then the house lost a leg and I can't get the boiler to run. No way to test it. Great timing.

    I didn't see rebuild kits for this type of valve on the link you gave me.