GB-142 install

Ted_9
Ted_9 Member Posts: 1,718
Keith, the pic is huge and hard to see. Can you go back and edit it by unchecking the box that will display the pic. thanks. but, is there a trap on the 3/4 pvc line. Not at the bottom after that tee, but up high. If not, it looks like combustion could leak out through the grey drain fitting.

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=373&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>

Comments

  • Keith_23
    Keith_23 Member Posts: 17
    GB-142 install - Any suggestions

    I did research on boilers and decided that a mod/con with non cell PVC vent was cheaper and more effecient than a sealed combustion boiler with a stainless chimney liner. I chose the GB-142.
    First problem, I could find noone in the area who would/could install a GB-142( "we cant do that", "pushing into the expansion tank is fine"). And Buderus does not yet have a reccomended contractor list.

    So I got my plumber to install it. I married the boiler to 3 existing zones. I am using a TACO 503 controller, grunfos pumps and a slew of valves (See pix).

    My plumber has installed other boilers but never a mod/ con. He did not do a combustion test or a gas pressure test or ionization current check. We flushed all zones for about 30 minutes each and he fired it up. Its running and seems to be doing well. I would love to scour out someone to do the above tests but am not sure I can find them in my area. Also what else should I do?

    Keith
  • Keith_23
    Keith_23 Member Posts: 17
    GB-142 install

    Ted;
    Thanks for the reply and sorry for the huge pic, I'll try to fix it. No there is not a trap and I see what you mean. Its piped like they had in the installation manual minus the box up top (Buderus said it wasn't needed).

    I guess I would have to redo the line with a trap for both the air gap and for the exhaust take off.

    Keith
  • Mark Hunt
    Mark Hunt Member Posts: 4,908
    Keith


    First, you'll glad you went with a mod/con!

    That trap has to be before you tie the boiler condensate in. Flue gas can blow down that 3/4" pipe and out of the gray fitting, there is nothing to stop it. Please move the 3/4" trap so that it is before the boiler condensate tie in.

    Mark H

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Keith_23
    Keith_23 Member Posts: 17
    Thank You

    Thanks a lot guys. I turned it off until I get the trap in on Monday. Still mild here in VA.

    Keith