engineer speced out pvc venting & intake lines thru roof for minuteman h.w. boilers . is this kosher ? thanx, bob

Comments

  • tk_3
    tk_3 Member Posts: 36
    PVC ................................NOT

    Do not use PVC to vent the Minutemam. This boiler requires AL294C vent pipe only!!!!!! This boiler does not have efficiencies above 90% therefore it is a non-condensing boiler. Vent temp's too hot for PVC.
  • Like Ron said.....

    No PVC for venting flue gasses. It can be used for the Air Intake though.

    Glenn Stanton

    Manager of Training

    Burnham Hydronics

    U.S. Boiler Co., Inc.
  • bob young
    bob young Member Posts: 2,177
    pvc not

    THANKS MUCH GLENN & RON for the quick response. i figured as much but some hot shot engineer without a train had a better idea. might redesign & put units in bsmt where they belong. bob