Vaporstat Setting
Steve Garson_2
Member Posts: 712
What are the symptoms of over-firing? The boiler is an SGO-4 with the 1.10 gpm nozzle that came with the package. Would the next step down be a 1.0?
Steve from Denver, CO
0
Comments
-
Vaporstat Setting
I just installed a Vaporstat on my new one-pipe steam system to lower the pressure to reduce vent whistling.
I had it set with a 4-oz cut-in and 10-oz cut-out. At this setting, the system heated all the radiators, but there was some whistling at the last moments of the steam cycle.
I dropped the cut-out to 8-oz and there was no whistling, but the system cuts-out on pressure and then cuts back in three times in just a few minutes before the thermostat is satisfied.
Should I be raising the cut-out or lowering the cut-in pressure. The radiators are all hot before the steam cuts off, it's just that the thermostat is not satisfied.
Thanks,
SteveSteve from Denver, CO0 -
The boiler
may be slightly oversized for the system. Try having a pro down-fire it a bit.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements