min height for chimney burning natural gas

U2WATCHER
U2WATCHER Member Posts: 9
DOES ANYBODY KNOW WHAT IS THE MIN. HEIGHT OF A CHIMNEY OF AN ATMOSPHERIC DRAFTED BOILER TO THE TOP OF THE CROWN OF THE CHIMNEY. I CAN NOT FIND IT IN THE NATIONAL FUEL GAS CODE BOOK.

Comments

  • Ron Schroeder
    Ron Schroeder Member Posts: 998
    I might not have this complete as

    it is off the top of my head but 2 feet higher than anypart of the stucture within 10 feet. so if you go up next to a roof you neeed toi be 2 feet higher than the highest side at ten feet away.
  • S Ebels
    S Ebels Member Posts: 2,322
    Hmmmm

    Are you trying to find out what the shortest allowable total height is?
  • U2WATCHER
    U2WATCHER Member Posts: 9


    > it is off the top of my head but 2 feet higher

    > than anypart of the stucture within 10 feet. so

    > if you go up next to a roof you neeed toi be 2

    > feet higher than the highest side at ten feet

    > away.



    I THINK ITS 3 FEET ABOVE ROOF AND 2 FEET ABOVE ANYTHING WITHIN 10 FEET
  • Joe Grosso
    Joe Grosso Member Posts: 307
    Height

    Also, the horizontal connector can't be more than I believe 2/3's of the height of the stack.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • U2WATCHER
    U2WATCHER Member Posts: 9


    > Are you trying to find out what the shortest

    > allowable total height is?



    I WAS ON A JOB TODAY AND B VENT ROTTED OUT.I LOOKED OUTSIDE AND BOILER INSTALLED REALLY IN CLOSET OUT SIDE OF HOUSE AND CHIMNEY IS GOING THOUGH ROOF ABOUT 4 1/2 FEET
  • S Ebels
    S Ebels Member Posts: 2,322
    So the total height.......

    So the total height of the chimney is how many feet? To get a good answer you'll need to know the stack diameter and the BTU input of the boiler also.
  • hr
    hr Member Posts: 6,106
    Would it be

    the length needed to get the draft reading the manufacture requires?

    Did you check NFPA 54?

    hot rod

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Vent has to be a minimum

    of 5 feet above the draft hood outlet. NFPA 54 National Fuel Gas Code(2006) section 12.6.2.3 page 54-97.