hot water heating stumper
bovide_4
Member Posts: 161
Description:
hot water system, convector rads, new Hoffman #54 auto air vents
house is 70' x 30' 2 floors + basement
boiler approx. 140mbh, mediocre install, supply 1", return 1 1/4", circ. on return, hoping to correct in the spring/summer.
old system, 1 1/2" supply manifold with twelve 3/8" copper tubing runs, one for each convector rad. same for the return.
Taco 007 circ was there before. Changed to a BG100, and only 1/2 of the rads get hot(same thing).
What did I miss?
hot water system, convector rads, new Hoffman #54 auto air vents
house is 70' x 30' 2 floors + basement
boiler approx. 140mbh, mediocre install, supply 1", return 1 1/4", circ. on return, hoping to correct in the spring/summer.
old system, 1 1/2" supply manifold with twelve 3/8" copper tubing runs, one for each convector rad. same for the return.
Taco 007 circ was there before. Changed to a BG100, and only 1/2 of the rads get hot(same thing).
What did I miss?
0
Comments
-
Mini-tube
Did you power purge each loop? I ask because it sounds like an air problem.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
sounds like....
air.
flush the system?
any valve lock?0 -
air
Did you get all the air out ?What pressure is the system under? Are the convector valves open? Most are butterfly valves .....Are they just spinning with bent stops?0 -
There are stop and waste valves on the return manifold. There is 20#'s at 180 deg. I will try power purging it. I was hoping the Hoffman 54's would do the trick, but the 3/8" tubing could have a lot of dips. Will try a BG 36 if all else fails, but I don't want to be an example in Dan H.'s next book about some poor slob who instinctively oversizes the circulator.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements