Steam radiators are hot upstairs & cold downstairs,WHY?
Jim_21
Member Posts: 3
Frustrating??!! Can anyone PLEASE tell me why my upstairs steam radiators get hot completely and my downstairs radiators where the thermostat is, barely get warm? I have all new gorton vents in em,and I hear them venting. I put two #1's on the two mains in the basement as recomended.
The burner appears to run short but frequent cycles.
When I first fired the system up the beginning of the season
it seemed to work perfect!!??
The burner appears to run short but frequent cycles.
When I first fired the system up the beginning of the season
it seemed to work perfect!!??
0
Comments
-
but is the system balanced?
do the smaller radiators have smaller air vents, and the larger radiators larger air vents?0 -
Try
using larger vents in the slow radiators.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Or.....
Is there a programmable thermostat that is still setup for forced warm air?(it IS the factory setting for most)This will cycle the burner about 4-6 times per hour, where a Gravity hot water setting wil cycle far less frequently, for longer periods.Probably the most found mistake on a new T-stat install IMO.
Next would be adjustable vents for the emitters. Let the 1st floor go a bit faster than the second floor, and adjust accordingly to get the proper "balance". Let the pigeons fly on the mains and fine tune at the radiators. This is most definately more art than science, and it takes quite a while to get it tuned in to every particular home.
Good luck and let us know how you make out on this. Chris0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements