Banging Wirsbo telestats on shutdown
Rocky
Member Posts: 121
Any one else getting this lately? As telestat goes to shut down, you get hammer in line. Usually a larger pump, (grundfos 26-64 etc). Have gone to replacing the motorized telestats with the thermopile style. Slower acting so you don' get the valve being hammered by pump flow. What are you guys doing for this?
Rocky
Rocky
0
Comments
-
banging telestats
Sounds like you have the telestats on the supply side. I dont usually find any problem when there on the correct side of the system
0 -
Pressure bypass
valves will work, especially when using large pumps like the 26-64.
Another quick trick if available, have an extra port on the manifold not connected to any radiant floor loops, just a 3 foot piece of pipe connected from supply to return and the valves slightly cracked open. It will allow a small amount of flow and bypass the pressure to allow proper operation of the telestats;
Or move the telestats to the return side of the manifold.
0 -
Need a PAB
with that much pump. (pressure activated bypass) It will cure the banging and allow better flow under small loads (one or two zones calling) Properly adjusted it is always bypassing some flow when zones start closing off.
Keeps the velocity noise down. Danfoss, Oventhrop, and Honeywell have them available. Most radiant manufactures have them in their catalogs, RTI does.
Standard equipment on the Danfoss ZCP zone panels.
The link below helps explain the mechanics better.
http://www.pmmag.com/CDA/ArticleInformation/features/BNP__Features__Item/0,2379,29498,00.html
hot rodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I'd bet a dozen donuts....
that this manifold is piped bass ackwards. In all my years, I've only seen one Wirsbo manifold hammer, and it had its supply and return line flip flopped somewhere between the mechanical room and the manifold. UN-floppped them in the mechanical room and noise went away. Check delta T with zone running and tell us what you find.
PAB's are still a good idea, especially when you have a pump with large cajones like you have. It keeps exces velocity noise probelms to a minimum.
ME0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements