Any one else getting this lately? As telestat goes to shut down, you get hammer in line. Usually a larger pump, (grundfos 26-64 etc). Have gone to replacing the motorized telestats with the thermopile style. Slower acting so you don' get the valve being hammered by pump flow. What are you guys doing for this?
Rocky

Comments

  • tim from Reed Wright
    tim from Reed Wright Member Posts: 113
    banging telestats

    Sounds like you have the telestats on the supply side. I dont usually find any problem when there on the correct side of the system
  • Dave Holdorf
    Dave Holdorf Member Posts: 12
    Pressure bypass

    valves will work, especially when using large pumps like the 26-64.

    Another quick trick if available, have an extra port on the manifold not connected to any radiant floor loops, just a 3 foot piece of pipe connected from supply to return and the valves slightly cracked open. It will allow a small amount of flow and bypass the pressure to allow proper operation of the telestats;

    Or move the telestats to the return side of the manifold.
  • hot_rod
    hot_rod Member Posts: 23,400
    Need a PAB

    with that much pump. (pressure activated bypass) It will cure the banging and allow better flow under small loads (one or two zones calling) Properly adjusted it is always bypassing some flow when zones start closing off.

    Keeps the velocity noise down. Danfoss, Oventhrop, and Honeywell have them available. Most radiant manufactures have them in their catalogs, RTI does.

    Standard equipment on the Danfoss ZCP zone panels.

    The link below helps explain the mechanics better.


    http://www.pmmag.com/CDA/ArticleInformation/features/BNP__Features__Item/0,2379,29498,00.html


    hot rod
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • I'd bet a dozen donuts....

    that this manifold is piped bass ackwards. In all my years, I've only seen one Wirsbo manifold hammer, and it had its supply and return line flip flopped somewhere between the mechanical room and the manifold. UN-floppped them in the mechanical room and noise went away. Check delta T with zone running and tell us what you find.

    PAB's are still a good idea, especially when you have a pump with large cajones like you have. It keeps exces velocity noise probelms to a minimum.