What are specs. on ATAG 443.068.40 pressure switch.
Comments
-
Did you try their website for spec info?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
-
Are you talking about this water pressure sensor? A Rinnai part?
0 -
are you troubleshooting something on a specific piece of equipment or are you trying to use this part in a different application and need specific info? Generally for troubleshooting a piece of equipment you need to use the info from that manufacturer, I believe this is made as an OEM part for rinnai and possibly other manufacturers. Point being the exact spec of the part might not be the info you need to troubleshoot the equipment.
0 -
This came off from a Rinnai boiler. Getting a E07 error. Cking output with meter on ohms is 8.853K. Nothing on the input side. I believe it is bad.
0 -
It is a Huba pressure switch 505.99037
0 -
According to the web the 07 is a problem with the heat exchanger temp sensor for rinnai? do you have a manual for your unit there? it's pretty easy to tell if the pressure sensor is bad, just verify the actual pressure in the unit and compare it to the pressure it shuts the unit down at. if the system is above that number and still shut down on low water the sensor is likely bad or detached. If you are getting the heat exchanger temp sensor fault its not this part
0 -
Looks like it may have a variable output. So depending on the pressure 0 to 4 bar (1 Bar = 14.5 PSI) the output would be 0.5 VDC to 3.5 VDC. The resistance of 8853 Ohms may be normal.
Also the internet says " Rinnai 443.068.40 2T85 Water Pressure Sensor 8 bar " Which may be a maximum safe pressure before damage occurs.
https://www.bonanza.com/items/like/1645335708/Rinnai-443-068-40-2T85-Water-Pressure-Sensor-8-bar
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0
Categories
- All Categories
- 86.8K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 106 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 104 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 952 Plumbing
- 6.3K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements