transformer voltage(s)

ron
Member Posts: 308
what are the voltages used for the [low voltage] transformers used in HVAC that wire to thermostats and taco zone valves or other equipment? Are they all "24VAC" or are there also 26, 28, 30, 40... volt ones?
I am NOT asking about the VA (volt-amp) rating.
In probing various places with a meter, I am reading 26 to 30 volts I'm guessing induced voltage?
I am NOT asking about the VA (volt-amp) rating.
In probing various places with a meter, I am reading 26 to 30 volts I'm guessing induced voltage?
0
Comments
-
They’re listed at 24, but can always test a little higher if good. Lower, badsteve0
-
24VAC is most common in the HVAC world. It is not unusual to see them read 30V. Depends on the load and input voltage also.
You can purchase more accurate models but they can be $$Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
@ron,
24 volts is the standard "nominal" voltage. Normally it is considered ok to supply voltage to a piece of equipment that is 10% higher or 10% lower than the equipment nameplate.
Transformers operate on the ratio of #number of turns of wire in the primary circuit to the number of turns of wire in the secondary circuit.
So a transformer rated 120 volt primary and 24 volt secondary would have a wire ratio of 120 x 24. Feed it with 120 volts you should get 24 volts out of it. The 24 volts may read slightly higher, say 26 volts with no load on the transformer.
If the transformer is rated 120 x 24 and the primary voltage is only 115 volts (about 4.5% low) then the secondary would be about 4.5% low or 22.9 volts.
Overvoltage would do the same thing. A 120 x 24 fed with 125 volts would be about 25 volts on the secondary.0 -
As the incoming fluctuates so does the output.
110 Volts + 15 % = 127
24 Volts + 15% = 280 -
I would expect the secondary to also vary with load.
A transformer unloaded should read higher than one near it's maximum capacity.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
To which I would add that generally they are supposed to be designed to deliver rated voltage at rated load, with the rated nominal voltage input. Small, cheap ones may droop a surprising amount between no load and rated load.ChrisJ said:I would expect the secondary to also vary with load.
A transformer unloaded should read higher than one near it's maximum capacity.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
i guess my question is... for "low voltage hvac transformers" they are all spec'd @ 24vac for the secondary, but any xfr < ~40vac secondary would likely operate any thermostat and heater zone valve just fine?
i see at supply house the filter has 24vac, 26.5 v.o.c, 27v.o.c. and 27.5 v.o.c. voc = voltage open contact. everything in hvac is low voltage (~24vac) secondary transformers? and doorbells?
0 -
what VA rating would be appropriate to run 2 taco 570 (gold) heater zone valves?0
-
I see from your comment that you have a slight confusion between the voltage output rating (Volts AC) and the available power rating (Volt-Amperes) of these gadgets. Unhappily, they both are sometimes abbreviated as "VAC" which is no help; the Volt-Ampere -- power -- rating should be abbreviated VA.
To directly answer one of your questions -- almost all HVAC controls are intended for a nominal 24 volts AC, unless they are specifically marked for "line" voltage -- that is a nominal 120 volts AC in North America. You can determine the power rating you need by determining the current draw of the device -- such as a zone valve -- and multiplying it by the rated voltage. But beware: some devices, such as some zone valves, are intended to operate on line voltage supplied through a relay from the low voltage control.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Volts X Ampsron said:what VA rating would be appropriate to run 2 taco 570 (gold) heater zone valves?
If the valve has a .9 amp rating X 24V = 21.6VA each
So technically, by the numbers 2 valves on a 40VA transformer.
Considered an intermittent load, you will usually see wiring diagrams showing 3 actuators wired to a 40VA transformer.
If all 3 happened to call at the same time from a cold start condition, you would have 21.6 x 3 = 64.8
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- 120.3K All Categories
- 83.6K THE MAIN WALL
- 2.8K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 414 Carbon Monoxide Awareness
- 30 Chimneys & Flues
- 1.7K Domestic Hot Water
- 4.6K Gas Heating
- 114 Geothermal
- 152 Indoor-Air Quality
- 2.9K Oil Heating
- 49 Pipe Deterioration
- 736 Plumbing
- 5.2K Radiant Heating
- 357 Solar
- 13.8K Strictly Steam
- 3K Thermostats and Controls
- 50 Water Quality
- 36 Industry Classes
- 70 Job Opportunities
- 14 Recall Announcements