CSD-1 applicability question
SWEI
Member Posts: 7,356
I had understood that CSD-1 did not apply to boilers smaller than 400 MBTU/hr. As I start to read <a href="http://archive.org/download/gov.law.asme.csd-1.2009/asme.csd-1.2009.pdf">http://archive.org/download/gov.law.asme.csd-1.2009/asme.csd-1.2009.pdf</a> I see CG-130 excluding really large boilers and swimming pool heaters, but CG-140 goes on to lay out a somewhat complex series of conditions for listed boilers under 400 MBTU/hr.
CG-140 (1) requires two things:
Compliance with all of part CW
Is this something we need to verify on a case by case basis?
Compliance with two specific paragraphs of CE-110
CE-110 (a) requires a lockable disconnect "at the boiler" and an external boiler room shutdown. The first aligns well with both NEC and mechanical codes. The second seems to imply that I need to include a solenoid-operated gas valve (as interlocked with kitchen hoods) on the plant main?
CE-110 (i) apparently forbids self-resetting controls after the primary?
CG-140 (1) requires two things:
Compliance with all of part CW
Is this something we need to verify on a case by case basis?
Compliance with two specific paragraphs of CE-110
CE-110 (a) requires a lockable disconnect "at the boiler" and an external boiler room shutdown. The first aligns well with both NEC and mechanical codes. The second seems to imply that I need to include a solenoid-operated gas valve (as interlocked with kitchen hoods) on the plant main?
CE-110 (i) apparently forbids self-resetting controls after the primary?
0
Comments
-
CDS1 interpretation?
As i read it, you must has a lockable d/c at the appliance plus the emergency d/c either immediately outside the CAZ or just inside the door if it opens to the outside. one d/c per door.
If the d/c kills the power OR the fuel, it is ok.
Yep, looks to be all safeties on the other side of the system only. That mean a trip would kill all the power to the unit.
2009 IRC Table E4101.2 lists the disconnecting means per the appliance application. >1/8HP motor requires lockout d/c within sight of the equipment.
The 2009 IRC references CSD-1 and the ASME Boiler and Pressure Vessel Code Sections I and IV. Anyone have a copy of this Code?0 -
CSD-1
CSD-1
In regard to the switches at boiler room doors. Our inspectors here have only required the switches to shut of the control power thus shuttig off fuel.
I persoanly like to use the red commercial push buttons with legend plates "Emergengy Push to Off". In commercial buildings (schools) we installed the switches inside the boiler room doors.
There has been no mention of a gas solenoid valve separate from the boiler gas train. Shutting down the power effectively kills the fuel supply.
CSD-1 has not been separately adopted by all states. However, it has been adopted by the International Mechanical Code and I have been told also by the Uniform Mechanical Code as well.
I hope ASME does get after you for publishing a Copywrited document. I had to pay for mine.0 -
CSD-1
CSD-1
In regard to the switches at boiler room doors. Our inspectors here have only required the switches to shut of the control power thus shuttig off fuel.
I persoanly like to use the red commercial push buttons with legend plates "Emergengy Push to Off". In commercial buildings (schools) we installed the switches inside the boiler room doors.
There has been no mention of a gas solenoid valve separate from the boiler gas train. Shutting down the power effectively kills the fuel supply.
CSD-1 has not been separately adopted by all states. However, it has been adopted by the International Mechanical Code and I have been told also by the Uniform Mechanical Code as well.
I hope ASME does get after you for publishing a Copywrited document. I had to pay for mine.0 -
I have paid for
(and continue to pay for) a small library of copyrighted documents.
The link to archive.org was mine. I can not take credit for the target.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements