Furnace cfm

Hello to all

What is the rule of thumb/how do you calculate how much cfm you need for a furnace. Like we say 400 cfm for each ton of cooling.

Thanks mike.

Comments

  • Big EdBig Ed Member Posts: 869
    Thumbs

    200 CFM's per 10K BTU's 80% plus ,150 CFM's per 10K BTU's 90% plus at a 55* rise
    I have enough experience to know , that I dont know it all