Oil burner blower

Our oil burner turns on then off. Ten seconds later the blower comes on again for about a minute. It happens like that each time.



It used to just come on then the blower woks stay on without that interruption



Suggestions ?

Comments

  • earl burnermannearl burnermann Posts: 126
    edited December 2013
    blower comes back on

    Although the call for heat has ended and the burner has turned off there is still heat in the combustion chamber that is re-heating the heat exchanger. If you have the mechanical type fan limit switch then when the temperature gets hot enough the fan switch reactivates and purges the heat out of the system.



    Check to make sure your filter is clean, that your vents are open, and that no one has blocked any of them with, maybe, a Christmas tree and gifts.
    If the women don't find you handsome, they should at least find you handy!
  • vent is clear and filter is new...

    vent is clear and filter is new...
  • WeezboWeezbo Posts: 6,232
    is this an older burner?

    could this be a belt driven model ? how about a picture of the burner or a model or manufacturers name of the burner.

    hard to sometimes think just where to start because not all burners are made the same.



    thanks...