Turbomax Storage - LIFO or Symmteric?

Good morning,

 

I’m looking at two Turbomax storage tanks which were to be piped in Last-In-First-Out order, according to spec.  The contractor piped them symmetrically instead. 

 

Can anyone tell me whether the symmetric piping arrangement will cause any problems, impact the lifetime, etc?  Should I have him re-pipe it?



Thanks in advance.

Comments

  • ZmanZman Member Posts: 3,517
    Not a problem

    I think a simple symmetric header will work just fine. The objective is even flow. Both piping strategies will accomplish that.

    Carl 
    "If you can't explain it simply, you don't understand it well enough"