zero PSI/ drained system

We had a rad refurbished recently, and in order to disconnect the unit, we needed to drain the system. Have reattached the rad and tried to bleed the system but nothing coming out. Checked the gauge and it's reading zero PSI. I believe the water valves are turned on. Thoughts on how to fix this? Cheers.

Comments

  • Jamie HallJamie Hall Member Posts: 6,655
    Sounds more like hot water

    than steam...



    But anyway, assuming it is hot water, if the feed valve is open you should see pressure build as water flows into the system.  If not, it seems to this simple-minded fellow that either there is another valve in there which is closed still -- or the water is going out as fast as it is going in.



    If it is steam, you should see water rise in the sight glass, sooner or later.  But then, if it is steam, there was no need to drain to replace the radiator...
    Jamie



    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.



    Hoffman Equipped System (all original except boiler), Weil-McClain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch