Condensate meter

gcp13gcp13 Member Posts: 117
Just repaired a few leaks on this system.

140-300 psi steam coming in, reduced with spence valves

To 5 psi for radiators then to condensate meter then to indirect drain

Comments

  • district steam

    5 psi is still a bit high for radiator/ main vents/traps to handle. can it be dialed down?--NBC
  • gcp13gcp13 Member Posts: 117
    Lower presure

    Yup,going back when heat is on to test return Lines

    & try to cut down the presure it may need that presure

    To push condensate back lots of back pitched lines
  • RJRJ Member Posts: 484
    steam valve

    The Old Spence amd hoffman press. reducing valves required a set horizontal pipe length coming off the outlet piping as well as the pilot piping, If the piping run was to short the valve may hunt and have a hard time maintaining lower outlet pressures.
    RJ
  • gcp13gcp13 Member Posts: 117
    Lower presure

    Thanks good info. Not sure how much we'll end up

    Doing. The piping is a mess but they have no

    Complaints about the heat