Testing & setting presuretrol

gcp13gcp13 Member Posts: 117
I made this device to test presuretrols and recalibrate

Them by adjusting the set screw until I get what I need

Leaving the fittings loose on tester lets the presure drop slowly

After it trips to see when it closes.

Works very well. I've had new presuretrols out of the box

Not shut off until 7 lbs. while it was set to 1lb.

Comments

  • BobCBobC Member Posts: 4,454
    great idea

    Honeywell should be embarrassed into doing something about this but because they have a monopoly they just continue to ship crap.It's a crime that they don't have any competition.



    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • Dan HolohanDan Holohan Moderator Posts: 11,877
    Great idea.

    Thanks for sharing. Seems a shame you have to do this on a brand-new product.
    Site Administrator

    [email protected]



























    Hug your kids.
  • gerry gillgerry gill Member Posts: 2,670
    Nice rig,

    i like it..yea we play with the calibration screw also..i think the first person laid off at honeywell at the start of the recession was the qa inspector.
    gwgillplumbingandheating.com

    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.