Bad TXV ?

Ambient temp 85° F , box temp( low temp) holding about 30 ° F. High super heat. Suction  presure 5 to 10  psi Head pressure around 225 psi . Evaporater frost (heavy) and evenly. Suggestion any one

Comments

  • RJRJ Member Posts: 479
    refrig

    What type of refrig,  walk in box or under counter,  what temp are you trying to maintain, are the derfost heaters oper.  what type control , low press. control or liquid line sol. valve, door gasket condition.  has someone been leaving door open.
    RJ
  • unclejohnunclejohn Member Posts: 861
    edited July 2013
    We fer sure

    Need every thing RJ asked and always start with a clear clean evap coil.