5" main
Gary_17
Member Posts: 37
Splitting 1 boiler into 2. Boilers only require 3" header. Will that work with the 5" mains or do we need to build 2 5" headers? Trying to avoid welding.
0
Comments
-
The boiler headers can be 3-inch
but the outputs from the boiler headers should go into a larger drop header. Dan has a diagram of this on page 67 of Lost Art.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Welded headers effect on boilers
Best to use threaded steel, as there is a little play in the joints for expansion and contraction, which could put undue stress on the sections, and their gaskets.
There is the same problem with copper headers.
Using a drop header makes it easier to fit, and avoid expansion problems.--NBC0