TT Prestige 110 exhaust

AdamAdam Member Posts: 400
I'm under the impression that you can run 2" exhaust and fresh air intake on the Prestige 110. I have a 24' horizontal run. Anyone done this? Any specifics I need to know?

Comments

  • SWEISWEI Member Posts: 7,356
    2" venting

    3" is better if you have the space.  From http://www.triangletube.com/documents/1/Prestige%20Vent%20Suppl_PVC_CPVC_PP%20_SS_0412.pdf



    2 Inch Vent Systems Restrictions for the PRESTIGE 60, 110 & Excellence.

    -    Derate the maximum boiler input by 3% when using the maximum equivalent length of 2 inch vent piping on Solo 110 & Excellence 110.

    -    The 2 inch vent system requires a 1 inch clearance to combustibles

    -    Use long sweep elbow to limit pressure drop and to avoid excessive vent temperatures.

    -    In 2 inch PVC vent applications, the first 7 equivalent feet of the vent system must utilize CPVC material.
This discussion has been closed.