Vent Sizing for 4" Mains.
MikeBlue
Member Posts: 9
I have four 4" mains running from our boiler, a Weil McClain 880. The boiler is running at 3 psi, and I am working to reduce it to 2psi. Before replacing all valves on 50 plus radiators throughout the 5 story building, which is my next project, I want to vent the mains properly. The current venting is as follows, but I am not sure if the current vents are working properly. Main 1 is 54' long with a Gorton #1. Main 2 & 3 are 36' and 48' and also are vented with Gorton #1's. The fourth is 65' long and vented with a Gorton #2. I would appreciate any suggestions. Thank you.
0
Comments
-
i'd put
4 gorton #2 vents on each main just for starters.gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
Venting
Hi Mike- It might seem at first that going from a single Gorton #1 to four Gorton #2s on each main was rather a big jump. However, when it is a suggestion by Gerry Gill, if it were me, I'd be ordering a shipment of Gorton #2s.immediately. You might also want to get Gerry's book on venting as it is extremely useful when working on vents and steam traps and will save you a lot of time and guess work.
http://www.heatinghelp.com/products/Books/5/146/Balancing-Steam-Systems-Using-a-Vent-Capacity-Chart-by-Gerry-Gill-and-Steve-Pajek
-Rod0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements