Pro Press with compressed air?

Has anyone used pro press to install compressed air systems? I'm thinking of 125psi top pressure in the system. About 400 lineal feet of 1 1/4" main with 30 or so 1/2" drops. Has anyone used pro press for this application?

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,455


    Yes we have done a to of it with no problem. If you read the ridgid web site it is approved for compressed air. There is however some stipulation on compressor oil.


    ED
  • Mike Dunn
    Mike Dunn Member Posts: 189


    I do it all the time. Rigid recommends that you use Type L copper and ProPress Gas fittings, as the O-rings in those fittings can stand up to the oils in the system.
  • jim lockard
    jim lockard Member Posts: 1,059
    Done

    Used Propress to make up some 2 inch copper (L) for air lines at a plant making trusses for houses and so far no problem. I called Ferguson and they provided the fittings and the spec sheets that made the designer/engineer happy. J.Lockard
  • hvacfreak
    hvacfreak Member Posts: 439
    IMHO...

    ....it may be the best application for this product line. I've wanted to say this since I saw this post a couple a days ago ( and I know others have too , lol ).