sizing indirect for new steam boiler

bob young
bob young Member Posts: 2,177
REPLACEMENT STEAM BOILER .ea too confined for independant water heaters. not familiar with sizing method to provide indirect domestic tank , etc. 14 families. need formula for additional btu load to add to steam boiler. thanx, bob nyc

Comments

  • kcopp
    kcopp Member Posts: 4,431
    No need to add....

    anything. No different that adding an indirect to a hot water boiler. No room for a tankless water heater?
  • Snowmelt
    Snowmelt Member Posts: 1,415
    Taco hvav

    John Barba has a nice webinar on how to size

    Also hotwater.com



    Tankless & in NYC see me.
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,525
    Tankless

    Consider takng a Find a Contractor ad.
    Retired and loving it.
  • icesailor
    icesailor Member Posts: 7,265
    Sizing DHY loads:

    Kind of an exercise in futility?

    Size the DHW load by the way it is supposed to be added to a boiler, then picking boiler for a 30,000 BTU load at design temperature. When the DHW load calculates to over 100,000?

    Its a "Phantom Load". Just put in a bigger indirect.

    SNARK Off.