tenant heat metering

Options
rjncont
rjncont Member Posts: 1
what is an accurate means to meter tenant heating from a central heat source (oil boiler)? all units are zoned individually 

Comments

  • Rich_49
    Rich_49 Member Posts: 2,766
    edited March 2014
    Options
    Taco

    Iworx system can be part of the system also because nobody will just take your math at face value .  You will also require a KNOWN Delta T . There are a few choices of circulator that will closely control Delta T . Taco VDT and Bumble Bee , also Wilo Stratos with IR option .
    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833
  • Big Ed_4
    Big Ed_4 Member Posts: 2,785
    Options
    Tenants

    We all know the best option is a separate boiler and oil tank
    I have enough experience to know , that I dont know it all
  • maine rick
    maine rick Member Posts: 107
    Options
    control

    we use Honeywell AQ control with communicating thermostats. you can set the max temp and check the amount of hours each zone runs. also is outdoor reset ready.