High Duty baseboard
scott10801
scott10801 Member Posts: 1
Can any tell me how many feet of high duty baseboard can be placed on a normal 3/4 loop. I know it's about 67 feet for standard output tube and fin
  • SWEI
    SWEI Member Posts: 7,356
    High Duty Basebaord
    I'm not familiar with that brand, but several manufacturers offer heavy duty or high output variants.  The length limit for a 3/4" circuit would depend on the flow, which would in turn depend on the ∆T for the loop.
  • kcopp
    kcopp Member Posts: 4,418
    Typically...
    40,000 btu on 3/4" copper. So if normal baseboard is around 600 btu/ ft that is around 66/67Ft.
    You could go more but your output will not be 600/ foot after the 67'.
    Typically high output is 750/ ft. (ie.. Sterling Senior)
    That puts you in the 53' range on 3/4" copper
  • Rich_49
    Rich_49 Member Posts: 2,766
    Beware
    of the disclaimer that  "this includes a 15% heating effect factor " ,. this is a fictitious number that should be subtracted , making 600 per foot actually 510 per .