Story of Chief Big Boiler and Cousin Little Pipe
Details of the system (and previous attempts at fixing things) can be found in the attached thread.
<a href="http://www.heatinghelp.com/forum-thread/149174/Complete-System-Review-Two-pipe-System-plus-One-pipe-Counter-Flow-Extension">http://www.heatinghelp.com/forum-thread/149174/Complete-System-Review-Two-pipe-System-plus-One-pipe-Counter-Flow-Extension</a>
That said, after performing all of the following:
-capping the return lines which were piped incorrectly,
-skimming the boiler,
-installing main vents,
-replacing & putting multiple vents on some of the radiators,
-adjusting radiator pitch,
-changing some supply valves,
-setting the thermostat's Heat Rate Cycle to 1,
-adding a vaporstat with a low pressure gauge, and (running between .5 - 1.5 for now)
- adding insulation to the near-boiler piping
I have the system to the point where the noise level doesn't startle the neighborhood too much anymore. That said, its not without sacrifices:
- the kitchen radiator still clanks viciously. No effort was able to overcome the mis-sized (3/4") runout to it (... and possibly badly pitched as well). Good thing its furthest room from the bedrooms
- I have to keep the supply valve shut for a bathroom radiator due to the same reason, adding to the oversized boiler issue i have to begin with. (55,410.14 needed vs. 145,000 that the Weil-Mclain EG-50 provides)
- short cycling still occurs, especially during recovery mode since I keep it cold at night.
While i try to find alternate solutions to the short cycling, in regard to the clanking, i read somewhere that, given the narrow size of the pipe, venting the radiator vvvvery slowly theoretically might help a bit. The give & take there is that is a radiator that is further away so if things were ideal, preference would be to vent it a bit quicker.
any thoughts? Given the flaws with the system anything i do is essentially a patch/workaround until i'm prepared to break open the walls and re-pipe.
thanks
  • BobC
    BobC Member Posts: 5,477
    edited February 2014
    slow might help
    I'd try the slow vents on the clankers, I think the maid o mist #6 is rated for 0.02CFM and you could probably slow it further by partially blocking the hole with a strand of wire. That might mean they don't heat like they should but maybe it will quiet them.
     Next I would stop using a setback and just crack a window in the room you want to stay cool at night. I don't think your saving enough money to matter unless the temperature is turned down for days.
    Bob
    3PSI gauge
  • Clank Clank
    Clank Clank Member Posts: 30
    Setback
    Thank you for the comments. Looking at the setback is certainly a thought. I didn't know enough about the savings to commit to making the change yet. I just posted another thread on the topic. thank you again. I'll follow your advise on the vent ... and let you know.
  • BobC
    ERROR
    In my post above I suggested trying a Maid O Mist #6 because of it's small removable orifice. The #6 is not slow it actually has a 0.15" orifice.
    I meant to tell you to use the Maid O mist #4 which does have the removable 0.028" orifice, the Hoffman 40 has a 0.04" orifice. I'm sorry if this led to any confusion.
    Bob
    3PSI gauge
  • Banging
    Keeping your supply valves to some radiators closed can cause banging and spiting out of the vents.
    Thanks, Bob Gagnoni