Is envelope heat loss linear to inside/outside delta T?

Options
markt
markt Member Posts: 26
I have a heat loss calc that says 10 btu/hr per square foot at interior temp of 74° and design day of 36°, an inside/outside delta of 38°.



If it's half that, ie, outside is 55°, presumably I need half the btu input at 5 btu/hr?

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 23,284
    Options
    That's the theory...

    anyway.  And it's probably close enough over the range we play with, given that there are large other variables we don't play with (like infiltration, or the effect of convection -- wind -- on boundary layer heat loss on the outside walls, and other esoterica...).
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • gennady
    gennady Member Posts: 839
    edited January 2014
    Options
    delta T

    Delta T is difference between 55F and outdoor temperature. 55F is design temperature of the envelope of the house. Heat is lost from envelope of the house to outdoor. But huge factor in heat loss are infiltrations. They might be larger than heat loss trough the envelope itself.