Honeywell Relay Replacement
BT123
Member Posts: 11
Hello-
Anyone know if I can replace a Honeywell R8184D with an R 8184G? I have a hydronic heating system and use this with an Aquastat Type8 Relay. It fires the furnace when a call for heat is initiated both throws the red reset switch sporadically.
Thanks!
Thanks!
I'd use a GeniSys 7505A
and jump the thermostat terminals. Its 15-sec trial for ignition is much safer then the R8184G or D's 45-second trial. Also, it turns off the ignition when the burner is running, saving electricity and electrode wear.All Steamed Up, Inc.
Consulting0 -
Thermostat jump
Can you explain jumping the thermostat terminals?
Thanks0 -
Maybe
It's doing exactly what it's suppose to do.Check and clean the cad cell per the instructions. Troubleshooting is A-B-C, starting with the simplest first.0 -
Cad Cell
Yep...Ive inspected the cad cell for cracks etc...and cleaned the lens. It "looks" fine to me...maybe its internal? Im replacing the cad tomorrow first, then if that doesnt fix it, will move to the controller.
Thanks for the advice-0 -
check cad cell eye ohms.
remove the cad cell eye leads from the ff terminals and check how many ohms the eye is seeing. If its over 1600 then it is the eye or something obstructing the eye's view.If the women don't find you handsome, they should at least find you handy!0 -
I appreciate
the advice. Ill give the ohms test a try.0 -
Read Oil Forum:
Read what I posted in the Oil Forum before you go out and spend a lot of money.
But do as you will.0 -
Checking Cad Cells:
Take the two yellow wires off the "F-F terminals on the 8184G and wire nut them to the leads of a multi-tester set on the Ohm Scale Have the transformer back. Ambient light should give you a reading. Put your finger over the eye. It should be an open circuit. Shine a light against the eye. It should go way up. If it doesn't, the eye and assembly could be bad. Is the plug part of the "eye" tight? I've changed more cad cell assemblies than I ever changed eyes.
Check for carbon buildup on the retention ring before you get nuts buying parts.0 -
BT123
Are you having that boiler properly serviced, every year?0 -
The last time
I had it serviced was two winters ago.0 -
I had to replace my honeywell
I replaced my honeywell on my Beckett AF oil burner with the 4009 series 45 second delay..I went thru all the tests with ohms for the sensor and also all the tests for the primary relay..and all showed good. I had an intermittent problem internally with the primary.
I thought I had a loose wire somewhere and tested all the wiring at all the junction boxes with the voltmeter. When I moved the primary relay around..on the side..laying flat..at an angle...it worked and then went on and off..etc..
Just remember this. I got prices for that relay that varied alot. The highest was $175..the next was $99 at home depot..the next was $77 at a local plumbing supply...the next was $68 at a burner supply...and finally the price I paid...$52 at a plumbing supply. That's a big range.
Everything in the instructions and PDF's included with new realay are there to show how to test the unit for all safety tests.
I am not a parts replacer either. I test everything first and find information on how to do it. My analysis in this case was correct and now the system problem caused by the bad primary relay has been corrected. I also was pointed in the right direction by following this site as well.0 -
Not Good
It's an oil burner. It needs to be serviced annually. Soot build-up kills heat transfer, and that wastes your money. The heat just goes up the chimney. There are configurations of oil filters that prevent crap from getting to the burner, which I'm sure are not on your boiler. The burner is probably gummed up with nasty stuff (technical term), at this point. Have it serviced, and watch the amount of crap that gets cleaned out of the boiler.0 -
Paul...
Thanks for the info....I did a visual inspection of the inside of the burner and it doesnt seem too bad...Im sure theres all sorts of build-up in the lines and such though. Im pretty handy...do you think its something I can do myself?
Thanks again for the advice
Brian0 -
Personally
I wouldn't play with the burner itself. Have a pro clean it, and set it up with a digital combustion analyzer. Watch what he does, and you make the call as to what you'd feel comfortable doing yourself.0