Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

EDR calculations

Options
Many buildings in NYC use the steam risers to heat the bathrooms and kitchens.

When calculating the load for a boiler, how do you calculate the EDR for the risers. In my case they are 2 inch pipes, 30 feet in length.

Thank you.

Comments

  • SWEI
    SWEI Member Posts: 7,356
    Options
    Two inch pipe

    measures 7.46" in circumference, or 0.62177 square feet per lineal foot.  30 feet would have an EDR of 18.65 square feet.
  • baylis
    baylis Member Posts: 6
    Options
    Thanks

    Thank You
This discussion has been closed.