aquastat setting

hairball
hairball Member Posts: 19
I have two aquastats. One maitains the maximum temp of the water in the furance the other wont let the thermostat in the living room turn on the ciculator pump unless the water temp in the furance it at a minumum temp. what should the second aquastat be set at?



Thank You



Chris

Comments

  • there are no

    There are no aquastat(s) on furance.. only boiler
  • hairball
    hairball Member Posts: 19
    oops

    My bad. Boiler then
  • hairball
    hairball Member Posts: 19
    Delta t

    Belive its calle the delta t. It maintains a minumum returune temp of the water.
  • Ron Jr._3
    Ron Jr._3 Member Posts: 603
    What model number is the aquastat ?

    And is the boiler making hot water with a coil ?
  • hairball
    hairball Member Posts: 19
    edited October 2013
    hot water

    Its and old richardson hot water boiler. No coil. Sorry all I can tell you is they are Honywell aquastats. You can see them at the top of the middle picture. They dont have the covers on them.
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,540
    20*

    A minimum of 20* less on the B aquastat,in reality with that POS you don't even need it!
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • billtwocase
    billtwocase Member Posts: 2,385
    aquastat

    Ever work on a Waterair? They had them
  • gennady
    gennady Member Posts: 839
    edited October 2013
    dual setting aquastat

    hi is a boiler limit, set at 180, lo is to prevent condensation, set at 140. lo is preventing circulator from pumping constantly cold water trough the boiler. it allows to heat portion of the water at the time.