Help for first time homeowner with Utica service question
ArtVandelayLEEDAP
Member Posts: 9
in Oil Heating
Hello,
First time homeowner here in NJ. I'm an energy engineer by trade and a tinkerer, and I want to see if The Wall thinks about trying to tackle an issue I just ran into with my Utica SFH3100WT oil boiler.
I ran the unit for the first time the other day since purchasing the home (~1800 sq ft Cape) in August. The burner kicked on, everything was going great, approaching steady state. I was using a Testo to take combustion readings, and it was looking pretty normal....~85% EFF, 5% O2, low CO ppm. Then, at about 4 minutes, I started to hear a surging "whoosh" sound happen every 3 seconds or so. At each "whoosh," I got a puff of combustion products out of the barometric damper (which was about 10" in front of my face...very comforting). I looked at the Testo, and the CO had spiked to 500 ppm and climbing, then the burner locked out.
I'm thinking that this was a gunked up nozzle because the unit had been sitting for about 2 months before I fired it. Does this sound reasonable? If so, is this the type of thing I DIY guy with a reasonable level of burner knowledge could potentially tackle? I've pulled the manual and I think I can clean things up....curious if anybody has any opinions about my ambition here.
Thanks for the help.
-Grant
-Grant
Boiler
Is the draft control working properly? What does the O2 go to when the soot-out happens?
Sounds like a clogged filter or nozzle. The boiler should absolutely be swept and cleaned at this point.0 -
Clogged oil line
You say everything was working ok and almost up to steady state when this problem happened. Sound more like an oil line restriction to me. As the unit runs with a clogged one pipe oil line, it slowly builds vacuum. Eventually, at low pressure, the oil begins to vaporize causing the pump's piston to slam shut. Once this happens the pressure in the pump rises and it relights. As this cycle continues the shut down due to high vacuum/low pressure will eventually starve the pump and the unit will shut down on safety. This is also causing soot to develop.There was an error rendering this rich post.
ahh...
One of the first things we might ask is how much oil , or did you "Stick the tank"...
on auto refill? might want that info prior to doing anything to 'Fix" it.0 -
Tech
Clean & Tune your appliance. If you don't know how, call a service tech.0 -
Oil line restriction
Definitely replace the oil filter and nozzle. Also, it's likely that the pump strainer will need to be cleaned or replaced.0
- 85.7K THE MAIN WALL
- 51 Biomass
- 71 Chimneys & Flues
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 60 Pipe Deterioration
- 850 Plumbing
- 5.8K Radiant Heating
- 375 Solar
- 14.5K Strictly Steam
- 51 Water Quality
- 38 Industry Classes
- 55 Job Opportunities
