Great Article

Options
CMadatMe
CMadatMe Member Posts: 3,086
From Ron Beck on short cycling Alpine Boilers in this month US Boiler Report. If your not getting this monthly suggest you subscribe.



<a href="http://origin.library.constantcontact.com/download/get/file/1113645395323-64/USBoilerReportOctober2013.pdf">http://origin.library.constantcontact.com/download/get/file/1113645395323-64/USBoilerReportOctober2013.pdf</a>
"The bitter taste of a poor installation remains much longer than the sweet taste of the lowest price."

Comments

  • Alan (California Radiant) Forbes
    Options
    I agree

    Another reason for heat loss calculations on all your jobs and not add anything to that number for an indirect.



    I see Alpine boilers come up quite often on The Wall, but have no experience with them.  Are they good?



    I subscribed to the US Boiler Report here:



    http://www.usboiler.net/news/?cat=21



    Thanks, Chris!
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • Zman
    Zman Member Posts: 7,569
    Options
    Indirect

    Unless you are using indirects with a very wimpy exchanger (amtrol)., I really have never seen this problem. Using Smart and Heatflo indirects the boiler can generally come up to full fire and run 10 minutes or so, satisfy the load and shut down. There is plenty of room for the boiler to modulate down if needed. Alpine boilers are not common here, maybe they have an issue I have not seen.

    Carl
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein