Harmonic noise changes from Rheem gas pack
Options
ellpats
Member Posts: 1
I have a Rheem two-stage gas pack with a scroll compressor. During the cooling cycle there is a constant and very obvious harmonic change in the noise coming from the unit.
0
Comments
-
Harmonics
How much time between normal noise and the hi/low harmonics? What is the voltage during this change ? What is the hi/low pressure? What is the SuperHeat during this change? Single phase or 3 phase?0
This discussion has been closed.