Beckett AFG Stalls

Options
vega
vega Member Posts: 2
Boiler fires right up , but stalls within about one minute. It was turned 10 months ago, even the  electrodes were changed.  But to be on the safe side , I  cleaned boiler, Changed filter, strainer and cad photo cell , Fuel lines were blown clean , fuel is bright pink. It fires up each time but won't remain on 

Comments

  • Steamhead
    Steamhead Member Posts: 16,832
    Options
    If you had to clean it out after 10 months

    it wasn't set up properly to begin with, You need a pro to fix this, but not the one that was there last time. Try the Find a Contractor page of this site. 
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • vega
    vega Member Posts: 2
    Options
    Beckett AFG Stalls

    Actually it didn't need to  be clean , since I was trouble shooting I figured I might as well vacuum it , there was no soot build up .It was the cleanest it's ever been. The nozzle , the strainer and filter were all in very good condition, none of them needed to be changed , I just thought if I was taken it a part I would changed everything that was easy to get too. I didn't want to make 4 trips to the store. Thanks for reading my post and replying to my situation   
  • JStar
    JStar Member Posts: 2,752
    Options
    Oil

    What were the combustion numbers?
  • Alan Welch
    Alan Welch Member Posts: 267
    Options
    Stalls ?

    A car stalls. Not an oil burner.  Are you having to push the reset every minute? or is the burner sputtering due to fuel supply issues (underground tank ? )  sounds like you need a good technician to troubleshoot , or we need more info  to help you diagnose.
  • Jim Davis_3
    Jim Davis_3 Member Posts: 578
    Options
    burner shutting down

    If you have a 2-line system the problem is simple, you are losing prime.  If that is a newer burner with the interrupted spark I would expect this to happen.  I don't recommend either one.  Need to go to single line or constant(intermiitent)  spark.
  • Ed N.Y.C.
    Ed N.Y.C. Member Posts: 73
    Options
    stalls

    oil is bright pink ? sounds like h2o in oil.should be red  ED N.Y.C.