replaced the steam boiler/ no vents on the mains un balanced heat?
vish
Member Posts: 9
Went to a job. House had 2 40yrs old steam boilers.One for up stairs one for main floor. The main floor boiler cracked. Removed both 86mbh and installed 1 125mbh. Measured the radatiors 375 sq ft. The new boiler has 365sq ft. The old boiler had no hartford loop or equalizer line no main steam vents. The system only heats 1/2 of the house . Would some main line vents help get the steam over there.
Vents are a must.
I am not a heating expert. I dont even play one on TV. It sounds like there were two independant steam systems originally. Are both steam circuits now connected to the single boiler? (My apologies if this question seems insulting.)
Everything I have read requires vents, and big ones at that, on the main pipes so that the steam reaches all the risers at the same time. Perhaps that steam is reaching only the radiator or radiators that are closest to the thermostat, and shutting off the thermostat before the steam reaches the remaining radiators.0 -
Pictures?
Post some pictures of the boiler, the piping around it, and how it is tied into the steam mains. Somebody might spot something.
Did you tie the returns together below the boiler water line?
3PSI gauge0 -
What you did is not ideal.
two boilers would have given zoning and a better efficientcy to the system. Photos would help diagnose it. Also the boiler is too small.Cost is what you spend , value is what you get.
cell # 413-841-6726
Pictures
Another vote for pictures.
Why would you take out two boilers and remove the ability to have two zones? My system is 392sqft connected to a 150mbtu boiler and I barely produce enough steam for the system.
Your setup may work but you need a ton of main venting and very slow vents on the radiators assuming its a single pipe system to keep radiators from hogging steam. If it is single pipe, what vents are on the radiators?Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
steam boiler /no vents
Thank You for taking the time. here are some pictures. Thanks Bob0 -
2into one no go
Put on plenty of gorton 2 main venting on the dry returns.
Clock the meter to determine the burner output is up to specs.
Compare your piping with that in the manual, as it seems to deviate from the instructions with a poorly-drained header. Iron is good though.
Insulate the supplies, and mains., even with fiberglass batts as a temporary measure.
Can you draw a diagram of the layout showing where steam is and isn't?--NBC0 -
bullhead tee
I'm with NBC on this one, separate the two mains and connect them into the header individually and then put a ton of main venting on each and you might just end up with a perfect system.
IMO you should use both risers out of the boiler and run them into a 3" header. If you look at the link in my signature my boiler is piped kind of how yours should be. You'll notice two mains connecting into the header.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Seperate the mains and tie returns below the NWL
I agree that you would be better off if you brought a separate riser to each main from the boilers header, tying the mains together is asking for problems. You need heavy venting at the end of each main or on each return. Calculate the volume of air in the mains and vent it so it expels all the air fast (1-2 minutes). Also it looks like a couple of returns are tied together above the waterline, that should be piped so they tie well below the boilers waterline.
Since the boiler is a little light for the load pipe insulation is not an option here, insulate all the piping you can after adding the vents and correcting the piping. Is this single pipe steam?
3PSI gauge0 -
Thank You
I will re pipe the header for individual lines coming off the header. Can I vent the mains where the returns come back?0 -
Thanks
thanks for the help. Bob0 -
Thanks Chris. worked perfect
Thanks Chris. worked perfect0 -
Vent it fast
You can put the main vents at the end of the main or at the return, just be aware you have to vent all the pipe between the boiler and the vent.Vent it fast and completely.
Hopefully it all works out for you.
3PSI gauge0 -
one boiler cracked. the other was not far behind
I should have taken some pictures of how this was.The customer has 2 kids in college and didn't have the money to re[lace both. I took out the tee and ran individual lines to a new header. put some vents in. Brought the main condensate lines down individually to a wet return below the water line. works great. The home owner has to insulate the supply lines to the 2nd floor there really heating the basement. The lines that were insulated really worked well. Thanks Bob0