Whining RBI 600 Dominator

Dave_132
Dave_132 Member Posts: 64
I have a copper boiler that has been in place for fifteen months . It provides both space heat as well as domestic hot water by way of a turbo max. The system is piped p/s through a low loss header. The gas pressures are correct and the flow rate is 20 degrees delta T across the heat exchanger at high fire. The system has not made up any water to speak of. The building is approx. twenty feet high to the top of the radiation. The system pressure is 18-20 PSI. Two weeks ago the boiler began to whine as it approached the set point of 175 degrees. The system did not appear to be dirty when the equipment was replaced. Why would this problem start now? I would appreciate any help
In a world of compromise , some men don't !

Comments

  • Whining system

    Is the boiler piped in rigid iron pipe for the gas supply?

    There has been mention here of a whine coming through the piping as a resulted using flexible gas line which had a certain resonance.--NBC
  • Dave_132
    Dave_132 Member Posts: 64
    Ridgid pipe

    Yes , the boiler is piped in ridgid pie and is properly sized
    In a world of compromise , some men don't !
  • Dave_132
    Dave_132 Member Posts: 64
    Ridgid pipe

    Yes , the boiler is piped in ridgid pie and is properly sized
    In a world of compromise , some men don't !
  • Dave_132
    Dave_132 Member Posts: 64
    Ridgid pipe

    Yes , the boiler is piped in ridgid pie and is properly sized
    In a world of compromise , some men don't !
  • Dave_132
    Dave_132 Member Posts: 64
    Ridgid pipe

    Yes , the boiler is piped in ridgid pie and is properly sized
    In a world of compromise , some men don't !
  • Dave_132
    Dave_132 Member Posts: 64
    edited December 2012
    Whining RBI 600 Dominator

    Yes , the boiler is piped in ridgid pie and is properly sized
    In a world of compromise , some men don't !
  • Mark Eatherton
    Mark Eatherton Member Posts: 5,853
    The fix...

    Common problem with copper and steel fin tube boilers, usually with glycol, but have seen it happen without.



    ME



    http://www.heatinghelp.com/forum-thread/143488/Water-treatment-for-copper-fin-snowmelt-system



    ME
    It's not so much a case of "You got what you paid for", as it is a matter of "You DIDN'T get what you DIDN'T pay for, and you're NOT going to get what you thought you were in the way of comfort". Borrowed from Heatboy.
  • Dave_132
    Dave_132 Member Posts: 64
    RbI whining boiler

    Thanks for the info Mark. I think you nailed the problem diagnosing buildup inside the tubes. I feel that after 15 months some type of film or scale has bonded and is causing localized flashing. What are your thoughts on valveing off the boiler and circulating a cleaner through the HX and then flushing. Would it be better to go after the entire system?
    In a world of compromise , some men don't !
  • Dave_132
    Dave_132 Member Posts: 64
    RbI whining boiler

    Thanks for the info Mark. I think you nailed the problem diagnosing buildup inside the tubes. I feel that after 15 months some type of film or scale has bonded and is causing localized flashing. What are your thoughts on valveing off the boiler and circulating a cleaner through the HX and then flushing. Would it be better to go after the entire system?
    In a world of compromise , some men don't !
  • Mark Eatherton
    Mark Eatherton Member Posts: 5,853
    Treat the system as a whole...

    Not that expensive and may circumvent other issues associated with the bio slime that may be fouling up the works.



    ME
    It's not so much a case of "You got what you paid for", as it is a matter of "You DIDN'T get what you DIDN'T pay for, and you're NOT going to get what you thought you were in the way of comfort". Borrowed from Heatboy.