Need help with controlling pumps

TLMTLM Posts: 22Member
I have just installed a Biasi B10-4 oil fired boiler with a Hydrolevel control to an existing system that has 3 zones controlled by Taco zone valves and a Smart 50 indirect on a pump. Supply house suggested a Taco ZVC 404 because I can allegedly control a DHW pump off of it on the priority zone. By following the wiring diagram we (electrician and myself) tied in the DHW pump and the system pump as per the Taco instructions. When one of the heating zones calls, the valve opens and the system pump does its thing. When the DHW calls both pumps come on. How do I get the system pump to NOT operate? I am not tied into the hydrolevel control cuz I figured the Taco board will control everything.
Mount Pleasant Plumbing and Heating Inc
· ·

Comments

  • ZmanZman Posts: 2,298Member ✭✭✭
    404

    I am assuming your DHW Circ is tied to the zone 4 N/O relay and the  system circ is to the extra TT?

    If the system circ takes it's power from the N/C side of the DHW relay that should do it.

    Just jumper from N/C to  TT were the power goes now. The system circ will lose power when the dhw energizes.
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
    · ·
  • TLMTLM Posts: 22Member
    404

    The system circ is tied into the extra rdy contacts along with the dhw circ. the dhw is on the com and n/c.
    Mount Pleasant Plumbing and Heating Inc
    · ·
  • ChrisChris Posts: 2,869Member
    Did you Jump

    3 and 4 on the priority zone where the zone valve would normally be used? Page 30..



    http://www.taco-hvac.com/uploads/FileLibrary/100-92.pdf
    "The bitter taste of a poor installation remains much longer than the sweet taste of the lowest price."
    · ·
  • TLMTLM Posts: 22Member
    404

    yes
    Mount Pleasant Plumbing and Heating Inc
    · ·
  • ZmanZman Posts: 2,298Member ✭✭✭
    404

    It will work as I described, The trick is to power 1 circ on no the other on nc. 
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
    · ·