ES2 venting?

jonny88
jonny88 Member Posts: 1,139
Hi and a happy thanksgiving.I got a ? with an ES2 Burnham.Usually when i put them in i use an Alliance for hot water.With the hurricane etc and loss of power for 2 weeks i am getting customers who want to use a hot water tank as they will have hot water in case of an outage.how do I vent the water heater into the same chimney as the ES2.The boiler comes with its own flue pipe.Is it possible to use a heavy gauge flue pipe to combine boiler and water heater eliminating supplied boiler vent pipe and run the two units into the new liner.Thanks for your time.

Comments

  • Steamhead
    Steamhead Member Posts: 16,796
    You should be able

    to put a tee near the chimney opening and tie both units in there. But first, is the chimney lined properly? ES2 boilers have low enough stack temps that an unlined chimney will run too cool, causing condensation in the flue.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • jonny88
    jonny88 Member Posts: 1,139
    liner

    i use the stainless steel liner sized to the specs.thanks for the reply just wanted to ensure the tee could handle the venting as the provided vent is double wall.i sometimes use the taco pc700-2 outdoor reset with this boiler,whats your thoughts on this.people seem to be happy with it so far.
  • Steamhead
    Steamhead Member Posts: 16,796
    The Taco ODR will work fine

    but we generally use the ODR card that Burnham sells for this boiler. It works just as well and saves some installation work.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,540
    SR501-ODR

    Take a look at the 501 w/ ODR, Burnham should reconsider their pricing on the EQ ODR module!
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • Jason_13
    Jason_13 Member Posts: 304
    IQ-ODR

    If I am using an IWH I find that the price is comparable to any other that has same features plus the ease of installation.