Please critique system

Options
stev0
stev0 Member Posts: 11
Hi all,

Piping Buderus gas cast iron boiler in primary/secondary. The manual gives no piping diagrams like on many other boilers. How's this look? Thanks for any feedback.

Steve

Comments

  • jim s_2
    jim s_2 Member Posts: 113
    Options
    Why primary secondary?

    Why not just supply and return?
  • stev0
    stev0 Member Posts: 11
    Options
    r

    gonna add one more zone on manifold for total of 3 and stub seprate short loop for future indirect. zones are small and just wanted to be on safe side
  • Charlie from wmass
    Charlie from wmass Member Posts: 4,322
    Options
    Buderus is fine with

    lower return water temps so primary secondary is not used. The design of the return port makes primary secondary piping redundant. Save the price of the pump for the third zone and just pipe it feed and return, unless you have some really cold return temps.